AS3010:2005 states that earthing of portable generators via earth stake is neither required or recommended.

You will actually sacrifice electrical isolation. I appreciate I have given you conflicting advice to Samste, but it is correct.

Don't buy an earth stake and root around with it at the field. It won't do anything for you except cost you time and money.